Tool Talk Discussion Forum
O.T.- KVA Interpretation
1945 A
10-07-2005 09:31:32
I need to install a transformer to drop from 480 V, to 120 V.
What"s the formula for figuring out how many amps it will safely handle?
This is for a control circuit, so there"s not a lot of current draw, but I seem to remember there"s a formula that tells you how much current this type transformer is capable of....
Thanks in advance!
Farmall_Ryan
10-07-2005 10:23:02
 Re: O.T.- KVA Interpretation in reply to 1945 A, 10-07-2005 09:31:32
The transformer should have a VA rating (or KVA). So say you have a transformer with a rating of 4800 VA or 4.8 KVA. That would mean the 480 volt side would be rated for 10 amps. 4800 VA / 480 V = 10A. Likewise, on the other side you can solve for amps 4800 VA / 120 V = 40A. Just remember that VA is a proportionality. 4 times the voltage will be 1/4 the current.
1945 A
10-07-2005 11:26:07
 Re: O.T.- KVA Interpretation in reply to Farmall_Ryan, 10-07-2005 10:23:02
This is a 1 KVA transformer.
Farmall_Ryan
10-07-2005 11:59:27
 Re: O.T.- KVA Interpretation in reply to 1945 A, 10-07-2005 11:26:07
Ok so if its a 1KVA transformer, assuming the high voltage side is 480V that would mean it is rated at 1000VA / 480V = 2.08 Amps. The (120)low voltage side would be 1000VA / 120V = 8.33 Amps.
1945 A
10-07-2005 13:03:27
 Re: O.T.- KVA Interpretation in reply to Farmall_Ryan, 10-07-2005 11:59:27
THANKS !!!
That's exactly what I needed to know!