Let me take a whack at explaining this. There are two considerations in selecting wire size. The first is heating. 10 AWG wire with the types of insulation normally used in homes is capabable of carrying 30 amperes without getting hot enough to create a fire hazard. That's why 30 amp breakers are used, so that any load that exceeds what the wire can safely carry will trip the breaker before the wire gets hot enough to be a problem. The second consideration is voltage drop. All conductors have some resistance. The longer the wire run, the more electrical resistance is encountered, and the greater the voltage drop for a given current. Remember, 120 volt tools don't like to run on 100 volts. I don't have my references at home, so can't give you an exact number, but if I were going more than a few 10's of feet I would use the next larger size wire just to make sure I didn't cause enough voltage drop to be a problem. Standard residential wiring is a split phase 120/240, 4 wire configuration. It is single phase, 240 volts between the two hot wires, with the neutral (and ground) in the center, which "splits" the 240 volt service to give 120 volts between the neutral and each phase. With your proposed configuration (2 hots, 1 neutral, one ground), and ignoring voltage drop issues, you could have two 30 amp 120 volt circuits, or one 30 amp 240 volt circuit, or some combination of 120 & 240 as long as the total current in each hot wire did not exceed 30 amps (for example, two 15 amp 120 volt circuits, one on each phase, and one 15 amp 240 volt circuit). You cannot connect the two hot leads together to double the current capacity, as this would short across the 240 volt input. The neutral never carries more current than ONE of the hot wires; when both hots are providing 30 amps, the currents in the neutral cancel, which is why the neutral is the same size as the hot wires. A ground wire can be smaller, since it only carries current in a fault condition, and then only has to carry it long enough to trip the breaker. By the way, actual loads are limited to 80% of the rated capacity, which means that in reality you could only draw 25 amps on each 120 volt circuit. By convention, power panels are rated for the allowable current in EACH hot conductor. A 60 amp panel is rated for 60 amps at 240 volts, which provides two 60 amp 120 volt feeds. If you really only want 30 amp service, that's fine, but using a 60 amp panel is overkill. I would STRONGLY suggest you go to your local library & find a book on basic wiring. They should also have a copy of the national electrical code. If you can't understand the code, you have no business messing around with something as dangerous as your household electrical service. Also, get a permit. Inspectors are generally a great resource, although I have to admit I've run across a few who had their own interpretations of some of the code sections. Inspections can be a pain, but it'll keep you from burning down the house or electrocuting yourself. By the way, just so you don't accuse me of blowing smoke, I'm a practicing electrical engineer with 30 years experience, and in a past life I designed power distribution systems for LARGE government communications facilities. Keith